Are you wanting to use open-circuit or closed-circuit charging? Currently I am using open-circuit charging. My charger settings are: Bulk/Absorb/Float: 55.8 V. Absorb set to 1 min. Since I'm not using SOC, rather voltage set points for my AGS, my triggers are Vstart: 50.9 @ 30 sec/51.0 @ 15 min. This starts the Generator (I'm completely off grid) around 20-22% SOC. My stop trigger is 54.5~7 (depending on how in-balance the batteries are) This gives me a 96-98% SOC. I would used the same charging values for SOC triggers. However, the Schneider AGS only allows for a 95% SOC. I've been playing with these numbers all winter and these are the best I've come up with after hours of charting voltage data.
Are you wanting to use open-circuit or closed-circuit charging? Currently I am using open-circuit charging. My charger settings are: Bulk/Absorb/Float: 55.8 V. Absorb set to 1 min. Since I'm not using SOC, rather voltage set points for my AGS, my triggers are Vstart: 50.9 @ 30 sec/51.0 @ 15 min. This starts the Generator (I'm completely off grid) around 20-22% SOC. My stop trigger is 54.5~7 (depending on how in-balance the batteries are) This gives me a 96-98% SOC. I would used the same charging values for SOC triggers. However, the Schneider AGS only allows for a 95% SOC. I've been playing with these numbers all winter and these are the best I've come up with after hours of charting voltage data.